KNX variable not sent cyclically despite “Send Value Cyclically” enabled
Hi,
I have a KNX variable for which I enabled cyclic value sending every 15 minutes, but the server does not seem to send the value to the KNX bus.
The relevant settings are:
- Value Type: 1.001 Switch
- On Connected: WriteToAddress
- Send Value Cyclically: True
- Cyclic Sending Delay: 15
- Transfer: True
- Write: True
- Read: False
I have attached a screenshot of the configuration.
We also have an independent KNX bus logger running, and there is no trace of any telegram from this group address being sent cyclically every 15 minutes. So it seems that the cyclic transmission is not being triggered at all.
Am I missing any additional setting required for cyclic sending?
Also, what is the best way to diagnose this in bOS? Is there any internal log or debug option where I can verify whether the cyclic write is actually being triggered?






The issue has been identified and resolved.
The problem was related to the KNXnet/IP (Falcon) driver. With this driver, the “Send Value Cyclically” function was not actually sending the KNX value to the bus.
ComfortClick support was able to reproduce the issue on a Grinder server as well.
The workaround is to change the KNX connection driver from:
KNXnet/IP (Falcon)
to:
KNXIP
After changing the driver, cyclic sending did not start immediately in my case, but after restarting the bOS server it started working correctly. The values are now being sent cyclically at the configured interval as expected.
So if anyone encounters the same problem:
ComfortClick has also created an internal ticket to investigate/fix the issue with the Falcon driver.
Many thanks to David and the ComfortClick support team for taking the time to reproduce the problem and find the actual cause.