change modbus setting through formula
Today my home has had a power outage.
My solar inverters are connected to my Jigsaw through modbus. It appears the modbus connection isn't restored after the outage, possibly because the inverers restart shortly after the Jigsaw-modbus is activated.
The solution seems to be to deactivate and reactivate the modbus through bOS (settings > driver > enable > false/true).
I'm now trying to make a fomula which is triggered after a reboot of bOS. The formula should deactivate and reactivate the modbus driver.
Any tips on how to deactivate and reactivate the modbus?
Or are there any other ways to reactivate the modbus connection?
Thanks for your support!
This not possible yet(through program), but hopefully it will be updated soon. Is the modbus error handling set to reconnect?