Comfort Click Jigsaw 3 and PLC bad communication
I would like to address an issue regarding the Comfort Click Jigsaw 3 device and the PLC controller. Communication is carried out through the Modbus TCP protocol. The initial problem involves the mobile application displaying the online status of the Comfort Click device, but it lacks successful communication with the PLC controller. Changes in values within the application do not reflect corresponding alterations on the PLC controller. This issue has been temporarily resolved by halting the operation of the PLC and restarting it, but it reoccurs after some time.
The second problem occurred today in the form of the unavailability of the mobile application. When attempting to log in to the device, an error is displayed: "Error connecting to server." Additionally, on the Comfort Click web platform, I noticed that the status of my controller is marked as offline.
I kindly request your expertise in diagnosing and resolving these issues.
Hello, current version of bOS configurator is 4.9.40 but I can't log in to my device because status of my controller is offline. It was online working perfect for few days and now it is offline and I don't have any clue why. I will check debug log but first I need to get my controller back online. Do you have any idea why controller when to offline when it was working for few days?
If the jigsaw is reachable on lan then the public address has changed? Do you use static wan ip or dynamic? It went offline probably because the IP has changed. You need to set the new public address again and correct port for it if you use custom port not the default 443 and set it as dynamic if needed.