MODBUS - BigEndian Vs LittleEndian
Hi,
I've this instrument EASTRON SDM630M
and i'm trying to read it in modbus.
Usually i start my test with modbus pull software.
I'm read the register number 4 - input register FC04 - (Voltage phase 3) in Floating32bit - BIGENDIAN

In comfortclick, to read the same value i need to set LITTLE-ENDIAN.


you can see that in BigEndian the value is incorrect.
Do you know why there is this different from Modbus Poll ?
Thanks in advice.
Modbus Pull start from zero like bOS.
I think there is an error name in comfortclick because endianess is a standard for reading and it can't be different.
In Big-endian the most significant byte (the “big end”) is stored at the smallest memory address
Address: 0x00 0x01 0x02 0x03
Value: 0x12 0x34 0x56 0x78
In Little-endian the least significant byte (the “little end”) is stored at the smallest memory address
Address: 0x00 0x01 0x02 0x03
Value: 0x78 0x56 0x34 0x12