Hey,

Our client wanted to change ventilation speeds from the thermostat. Ventilation runs on Modbus everything else is on KNX bus.

This may be a really stupid question but... i found that when i put a value for 1byte in bOS 1 then KNX sees it as 3 and value 2 as 5. But in bOS it shows the correct values. Ventilation has 3 speeds that we control (0 is for away, 1 is home, 2 is guests) I made some screenshots. 
In bOS

Image 1742

Shows as correct value in bOS

Image 1743

But in KNX sees it as 3 and value 2 as 5 in knx

Image 1744


Is this normal or am i missing something? 

I got it working though by changing the values in the Thermostat to 3 and 5, there is no problem with value 0 :) . So now every thermostat shows the correct status and from every thermostat they can change the ventilation speeds. But I find it weird that it changes the values like that.

Best regards.

Avatar
Jürgen Jürgenson

Yep that was it, thank you Noel. 

Best regards.

Avatar
Noel Fuentes

Hi,

Make sure the value type in bOS es set to the right type. If it's set to "scaling", bOS will interpret that as a percentage and so it wull send it that way to KNX. Maybe you should set it as "value1Ucount".

Best regards.