I've configured the physical address in knx for a Jigsaw to be 1.1.63, as the last device before a line repeater.

The issue is that when I open the bus monitor in ETS, I see a lot of traffic coming from 1.1.64, which is the line repeater, but corresponds to the Jigsaw.

Why isn't it using the address I configured?

Thanks in advance

Avatar
ComfortClick Support
  • Under review

Hello,

for the Jigsaw server, it works the same way as a IP interface. It takes 8 addresses after the one set in bos (e.g. if Jigsaw interface is set to 1.1.63 it will take addresses from 1.1.64-72)

Best regards,

Avatar
Gruyère Energie SA

Hello,

I have a similar problem with the Jigsaw.

I set the physical address to 1.0.60 but after a few minutes when I donwload  KNX device ETS ask me for change the physical address because the physical address is set automatically to 0.0.0 and I see on the bus monitor that the Jigsaw send telegram with 0.0.0.

Avatar
Jürgen Jürgenson
Quote from Gruyère Energie SA

Hello,

I have a similar problem with the Jigsaw.

I set the physical address to 1.0.60 but after a few minutes when I donwload  KNX device ETS ask me for change the physical address because the physical address is set automatically to 0.0.0 and I see on the bus monitor that the Jigsaw send telegram with 0.0.0.

Hey,

For me, it stays on the address i originally gave it 0.0.2 But when i open the settings the values are blank. On group monitor I can see that it's asking on 0.0.4 address.

Avatar
Gruyère Energie SA

First: I see that I have not the same option in menu. Why ???

second: Have you test if you change the KNX address to 1.0.xx ?

Avatar
Jürgen Jürgenson
Quote from Gruyère Energie SA

First: I see that I have not the same option in menu. Why ???

second: Have you test if you change the KNX address to 1.0.xx ?

1. I have updated mine to the latest 4.7.22 beta version

2. Noup not yet, I will try it later and give you feedback.

Avatar
Jürgen Jürgenson
Quote from Jürgen Jürgenson

1. I have updated mine to the latest 4.7.22 beta version

2. Noup not yet, I will try it later and give you feedback.

Ok, when i changed the address to 1.0.60 i lost connection to it. And device discovery is unable to find it again even if i changed it back to 0.0.2 like it was before. Rebooting jigsaw did not help. So yeah its strange.

Avatar
Gruyère Energie SA

Thanks Juïrgen for the test.

Contrariwise in my server I dont lose the connexion with another address, juste the address keep the value 0.0.0 in ETS

Now we are waiting for the response from comfortclick support.

Avatar
Jürgen Jürgenson
Quote from Jürgen Jürgenson

Ok, when i changed the address to 1.0.60 i lost connection to it. And device discovery is unable to find it again even if i changed it back to 0.0.2 like it was before. Rebooting jigsaw did not help. So yeah its strange.

I'm still having trouble finding jigsaws IP gateway. For testing reasons i connected a new 731 ip gw and this is found with jigsaw right away. The internal gateway is missing, i tried restarting, changing the address nothing seems to help.

Avatar
Gruyère Energie SA

I go up the post, because  is a problem with a KNX tolopogy.

Avatar
Maciej kahPEEtsa

Hello,