Modbus RTU fail
good morning, since the installation on the beta version grinder, there are repeated interruptions in the operation of Modbus RTU in the application there is a connection, but the controllers stop interrogating the devices, it is not enough to pull the controller from the USB socket because it has no effect, but without turning it off, turn off the connection and turn on and suddenly call back .
Hey,
What is the error handling set to? If its on reconnect try write to log instead. I've also noticed that if its on reconnect it wont actually reconnect fully but it will just stop asking for updates. If its on write to log then it still receives updates even if there is some no responses.
For one of my projects with reconnect option - it stayed connected for about ~8-10hours then it just wouldnt update even if it was connected - after modbus driver disable/enable it starts to update again.