Bad communication between Jigsaw and MIM-B19N (MODBUS SAMSUNG)

Avatar
  • updated

Hi everyone,

i have a jigsaw connected to a Modbus interface module MIM-B19N Samsung. I have the next parameters:

Image 3875

I attach the datasheet of this module to compare if you need:  Manual Interface MODBUS Maquinas clima Samsung.pdf


The question is that some times, randomly, the communication breaks down and we can control any of indoor units we have. In addition, i attach a screenshot of Jigsaw's logs:


Image 3877

I don't know if the problem is because of driver's parameters or firmware error. I will appreciate any help .

Thanks

Avatar
Costel Miron

Hi Jose, I've got the same error, trying to communicate with an energy meter and replacing the modbus dongle solved the issue.

Avatar
Jürgen Jürgenson
Quote from Jose Jiménez

If i put Big endian, the data shows this:

Instead if i put little endian, the data shows correctly:

I don't understand why i can read this value (register 75) but i can control, for example, on/off unit (register 74)

Try to rise the command delay and read delay.

Avatar
Jose Jiménez

If i put Big endian, the data shows this:

Instead if i put little endian, the data shows correctly:

I don't understand why i can read this value (register 75) but i can control, for example, on/off unit (register 74)

Avatar
Jürgen Jürgenson

Have you tried setting the data format to big endian?