Graphic spikes when bOS makes a backup
Hey clickers,
I'm having a weird problem again, Our client demanded graphics for every meter (C/H water, electricity and for the whole building ventilation system) and i noticed that when we did a backup of the bOS configuration or the server did a restart, we got weird spikes in graphics that sometimes where lower values and some were higher values. The water and electricity info is collected and readout by Anybus mbus to modbus and the ventilation values are collected with usb modbus dongle. Pic below has a week view but actually the value rises again after the server get the correct value again from Anybus.


The thing is that I've been watching the raw logs from Anybus and these spikes don't come from Anybus... And when i look at the database files I see that right after the bOS server comes up it writes a unknown value and 15minutes(thats the update time of Anybus) later it will update it to the correct one. How to get rid of them spikes and where to they come from? And as you see from the picture the spikes are random not every meter is affected by it. I now have corrected the value spikes manually.
So hey its me again and sadly it happened again.
It happened to ~10 meters most of the spikes happened on 3.04.19
I did fix all the graphics on 2.03.19 so day after the fix they returned... The server has been online all this time, no restart no backups after 2.03.19.
Apartment 37 el.day t2
Apartment 37 el.day t1
Same apartment but the value spike is on 5:31 and 1:46. Returns to normal.
Some more examples
Apartment 10 hot w
Apartment 32 heating
Apartment 38 el.night
I will leave the DB's as is right now. And will check next week if there's any new spikes.