Serial Port - No Ack Error
I'm trying to connect a Paradox security system to a CC Grinder, through a Paradox PRT3 module USB (COM3), and I'm getting a "Error connecting to device - No Ack" message" 10 seconds after connection, keeps trying to connect.
Can't figure if its a Windows problem (tried several configurations for flow control on port settings), Paradox configuration (Serial Port ON, Automation ON, ASCII Protocol, 9600br) or CC.
Any ideas?
Hello,
did you try these settings, found in the paradox manual?
*From paradox manual*
Programming Sections
The following describes the programming sections which must be set when the Printer Module acts as an interface between a control panel
and a home automation module using the ASCII Protocol.
To access the Printer Module’s programming mode:
STEP 1: Press and hold the [0] key.
STEP 2: Enter the [INSTALLER CODE].
STEP 3: Enter section [953] (DGP-848) / [4003] (EVO).
STEP 4: Enter the Printer Module’s 8-digit [SERIAL NUMBER].
STEP 5: Enter the 3-digit [SECTION] you want to program.
STEP 6: Enter the required data.
The Printer Module can also be programmed using the WinLoad Security Software (V2.62 or higher) or using the control panel’s Module
Broadcast feature. Refer to the panel’s Reference & Installation Manual for more details. Please note that the serial number can be located
on the Printer Module’s PC board.
Best regards.